the last few days we have had no hot water coming from our MEGAFLO DD170
it is on a timer and when we run taps, no hot water, but the boost function heated the water when pressed.
i swapped the two stems round in the tank, and then the boost stopped working, and the timed water worked again.
so i knew the stem rod was at fault. COTHERM type:TSE
i tried various plumbing merchants round trafford park, none anywhere, until i found one place, feckin £37 inc vat.
fitted that, all works again.
what i was asking is: what is the recommended time to have the timer kicking in at so we have water for a shower in morning, and a bath at night and wash the pots at tea time.
default was 2:15am - 7:15am on the HORSTMANN ECONOMY 7 timer but would that give me hot water in the evening?
thanks in advance.